Fire Retardant Cables
At present, in cable industry, Fire Retardant, Low Smoke Halogen Free (LSZH) OR Low Smoke Fume (LSF), Fire Resistant cables are all described as Fire Retardant & Resistant Cables
Fire Retardant
Fire retardant cables are designed for use in fire situations where the spread of flames along a cable route need to be retarded. Due to relative low cost, fire retardant cables are widely used as fire survival cables. No matter the cables are installed in single wire or in bundles, during a fire, the flame spread will be retarded and the fire will be confined to a small area, thus reducing the fire hazard due to fire propagation.
Low Smoke & Halogen Free & Fire retardant (LSZH)
LSZH cables are not only characterized by its fire retardant performance but also by its halogen free properties, thus offering low corrosivity and toxicity. During a fire, this cable will emit less smoke and acid gases which may damage the human being and expensive equipment. Compared with normal PVC cable, LSZH cable outperforms by its fire retardant properties, low corrosivity and low smoke emission properties, however, normal PVC cables has better mechanical and electrical properties.
Low Smoke Fume (LSF)
The low halogen content and low corrosivity of low smoke fume cables lies somewhat in between fire retardant cables and LSZH cables. Low Halogen cable also contains halogen but the content is much less than PVC cables. LSF cable is designed to reduce the spread of fire, toxic gases and smoke during fire. The LSF cable is usually manufactured from flame retardant PVC blended with HCL additive and smoke absorbent. These materials help improve the fire performance of the LSF cables
Fire Resistant
Fire resistant cables are designed to maintain circuit integrity of those vital emergency services during the fire. The individual conductors are wrapped with a layer of fire resisting mica/glass tape which prevents phase to phase and phase to earth contact even after the insulation has been burnt away. The fire resistant cables exhibit same performance even under fire with water spray or mechanical shock situation.
Fire Performance Class
The main concern for the cable in its fire survival properties are its flame spread, smoke characterization and gas toxicity. In American fire standard, the concern lies more on the first two and it differs from the European standard which concerns all these aspects. In USA, it is believed that the fire hazard is mainly due to CO toxic gas emitted and the heat release during the conversion of CO to CO2 during the fire. Therefore, to control the heat release is the most important concern for reducing the fire hazard. However, in European countries, halogen content, the corrosivity of the gases, the smoke density and the toxicity of the gas are equally important factors affecting the safety and survival of human during a fire.
The European Electrical Committee categorized the fire performance of the cables into three classes, namely IEC60332-1、IEC60332-2 and IEC60332-3. IEC 60332-1 and IEC 60332-2 are used to assess the flame propagation characteristics of a single wire. IEC 60332-3 is used to assess the flame propagation characteristics of bundled cables. Comparatively speaking, IEC 60332-3 for bundled cables is more demanding than IEC60332-1 for single wires
IEC 60332-1/BS 4066-1 (Flame Test on Single Vertical Insulated Wires/Cables)
This test details a method of test for the assessment of the flame propagation characteristics of a single wire or cable. In this test, a 60cm cable sample is fixed vertically inside a metallic box and a 175mm long flame is applied at 45o from a gas burner placed at 450mm from the top at the upper portion. The specimen is deemed to have passed this test, of after burning has ceased, the charred or affected position does not reach within 50mm of the lower edge of the top clamp which is equivalent to 425mm above the point of flame application. The test method is not suitable for the testing of some small wires due to the melting of the conductors during the time of application of the flame.
IEC 60332-3/BS 4066-3 (Flame Test on Bunched Wires/Cables)
IEC60332-3C describes a method of type approval testing to define the ability of bunched cables to resist fire propagation. In this test, a cable specimen, consisting of number of 3.5m lengths of cables are fixed to a vertical ladder tray where they are applied with a flame from a gas burner for a specified times under controlled air flow. Four categories (A, B, C & D) are defined and distinguished by test duration and the volume of non metallic material of the sample under test. The cable specimen is deemed to have met the requirements of the standard if, after burning has ceased, the extent of charred or affected portion does not reach a height exceeding 2.5m above the bottom edge of the burner.
UL Fire standard
If a cable can pass a specified UL fire standard, an UL performance verification mark can be applied onto the cable jacket, illustrating both the UL class and the number. There are four primary fire testing standards as follows:
CMP (Plenum Flame Test/ Steiner Tunnel Test)
Plenum rated cables meet the NFPA-262 standard (formerly known as UL910) which provides the most stringent requirement of all the tests. Cable samples on a horizontal tray in a tunnel type of chamber are burned at 87.9KW (300000 BTU/Hr) for 20 minutes. To qualify for a plenum rating, the cables must have the flame spread of less than 5 feet or 1.5 meters, with a smoke density during the test of (a) 0.5 peak; and 0.15 maximum averages. The CMP cable is usually installed in air ventilation duct and air return widely used in Canada and USA. The fire retardancy properties of CMP cable is much better than LSZH cable complying with IEC 60332-1 and IEC 60332-3..
CMR (Riser Flame Test)
Riser rated cables meets UL 1666. Cable samples on a vertical shaft are burned at 154.5KW (527500 BTU/Hr) for 30 minutes. To qualify for a riser rating, the cables must have the flame spread of less than 12 feet beyond the ignition point. This test does not look at the smoke density or toxicity. Riser cable is suitable for vertical shafts not defined as an environmental air plenum.
CM (Vertical Tray Flame Test)
General purpose cables meet UL 1581. Cable samples on an 8 feet vertical tray are burned at 20KW (70,000 BTU/Hr) for 20 minutes. The cable is deemed to pass the test if the flame spread will not extend to the upper portion and extinguish by itself. UL 1581 is similar to IEC 60332-3C, except for that the number of testing samples is different. This test does not look at the smoke density or toxicity. The CM cables are usually used in runs penetrating single floor. This cable cannot be installed in vertical pathways.
CMG (Vertical Tray Flame Test)
This general purpose cables also meets UL 1581. CM and CMG are similar, both recognized in Canada and USA. This test does not look at the smoke density or toxicity. The CMG cables are usually used in runs penetrating single floor. This cable cannot be installed in vertical pathways.
CMX (Vertical Tray Flame Test)
The restricted cable meets UL 1581, Limited-use. The test consists of 25 feet long ventilated tunnel. The cable is placed on a ladder inside the tunnel and the flame of 30,000 BTU/Hr is applied to the cable 15 seconds on and 15 seconds off five times for a total exposure to the flame of 1 minute and 15 seconds. To qualify for this test, after the test flame is removed, the cable can flame for not more than 60 seconds and the charred portion will not exceed by 25%. UL 1581, VW-1 is similar to IEC 60332-1, except for the difference in the time for flame applied. This test does not look at the smoke density or toxicity. The CMX cable is suitable for use in dwellings and for use in raceway. This cable cannot be installed in bundles and must be protected in metal conduit. This type of cable is the minimum requirement in commercial installations.
IEC60754-1/BS6425- 1 (Emission Of Halogens)
This specifies a test for determination of the amount of halogen acid gas, other than the hydrofluoric acid, evolve during combustion of compound based on halogenated polymers and compounds containing halogenated additives taken from cable constructions. Halogen includes Fluorine, Chlorine, Bromine, Iodine and Astatine. All these elements are toxic by its nature. In this test, when the burner is heated to 800℃, 1g sample is placed inside and the HCL is absorbed into water inside the chamber fed with air flow. The water is then tested with its acidity. If the hydrochloric acid yield is less than 5%, the cable is categorized as LSZH. If the hydrochloric acid yield lies between 5% and 15%, the cable is categorized as LSF. IEC 60754-1 cannot be used for measuring the exact HCL yield if it is less than 5% and thus cannot tell if the cable is halogen free or not. To determine if the cable is halogen free, IEC 60754-2 should be used.
IEC6 0754-2 (Acidity)
This test specifies a method for the determination of degree of acidity of gases evolved during combustion of cables taken from the cable sample by measuring its pH and conductivity. The specimen is deemed to pass this test if the pH value is not less than 4.3 when related to 1 liter of water and conductivity is less than 10us/min. When the HCL yield lies between 2mg/g and 5mg/g, a cable specimen can pass IEC 60754-1 but its pH value may be less than 4.3 and therefore will not pass the IEC 60754-2 test.
IEC 61034-1&2/ASTM E662 (Smoke Density)
This specifies a test for determination of smoke density. The “3 meter cube test” measures the generation of smoke from electric cables during fire. A light beam emitted from a window is projected across the enclosure to a photo cell connected to a recorder at the opposite window. The recorder is adjusted to register from 0% for complete obscuration to 100% luminous transmission. A 1 meter cable sample is placed in the centre of the enclosure and is applied with a fire. The minimum light transmission is recorded. The result is expressed as percentage of light transmitted. The specimen is deemed to pass this test (IEC 61034-1&2) if the value is greater than 60%. The higher the light transmittance, the less smoke emitted during a fire.
ISO4589-2/BS2863 ( Oxygen Index LOI )
This is a test for assessing the oxygen index of the material in accordance with the test method specified in ASTM D 2863-95 “Measuring the minimum oxygen concentration to support candle-like combustion of plastics”. At room temperature, when the oxygen content in the air exceeds the oxygen index, the material will burn by itself automatically. The higher the oxygen index, the more retardant the cable is. For example if the oxygen index of a material is 21%, it means that the material will burn by itself even at room temperature because at room temperature the normal oxygen content is 21%, In general, the oxygen index of a fire retardant cable exceeds 33%
ISO4589/BS2782.1 (Temperature Index TI for determination of flammability)
This is a test for assessing the performance of a material when it is tested in accordance with BS2782: Part 1: Method 143A and 143B. The oxygen index of a material will drop when the temperature rises. When the temperature rises and the oxygen index drops to 21%, the material will burn automatically. This temperature is defined as temperature index. For example, the temperature index at room temperature is 50% and when the temperature climbs to 150℃, the oxygen index drops to 21% and the coal will burn by itself automatically. The temperature index of the coal is defined as 150℃. In general, the temperature index of fire retardant cable exceeds 250℃.
NES713 ( Toxicity Index )
This is a test defined by Naval Engineering Standard which is a directed at the analysis of a specified set of gaseous species which are commonly present in the combustion products of materials used in military application and which may cause lethality at the time of a fire. In this test, a 1 g cable specimen are completely burnt inside a sealed chambers of volume 0.7-1m3 using a burner fed with air and gas to give a non-luminous flame. The resulting chamber atmosphere is quantitatively analyzed for a specified set of gases. For each gas, the measured concentration (Ci) is scaled up for 100g and the concentration is recalculated as though the combustion products are diffused into a volume of exactly 1m3. The resulting concentration (C8) is expressed as the ratio of critical factor (CF) which is equal to the concentration of this gas considered fatal to human for 30 minutes exposure. The ratio C8/Cf is summed for all gases detected to give the toxicity index. The higher the toxicity index, the more toxic the cable material is. In general, the toxicity index of LSZH material is less than 5. LSZH cable will also emit toxic CO and if the cable materials contain P, N or S, the toxic gases generated will even be greater. Thus, LSZH cable cannot be categorized as toxic free. CM, CMR and CMP cables in general contains halogen content which is essential for passing the strict fire retardancy testing. For example CMP is made from FEP which contains Fluorine and is much toxic than normal LSZH cable
IEC Fire Resistance Testing
Fire resistant cables are designed for maintaining circuit integrity during a fire. Both the IEC and the BEC adopted two different standards, namely the IEC 60331 and BS 6387. Comparatively speaking, the fire performance requirement for BS 6387 is more demanding.
IEC 60331 fire performance standard.
IEC 60331-1999 details a method of test for assessing the fire resisting characteristics of a cable. The cable is defined as fire resisting if , under the conditions of this test, it being assumed that the test flame intensity is of sufficient magnitude to destroy the organic material, no failure of any of the 3A fuses occurs and if the withstand voltage on completion is not less than the rated voltage of the cable. The cable sample is deemed to pass this test if no fuse was ruptured nor any lamps extinguished during the 3 hour flame application and on re energizing the cable after 16 hours.
BS6387
BS 6387 specifies the performance requirements for cables required to maintain circuit integrity under fire conditions. It details the following methods to categorize the cables according to cable withstand capacities.
Resistance to fire alone – the cables is tested by gas burner flame while passing a current at its rate voltage. Four survival categories are defined: Cat A (3hours at 650℃ ); Cat B (3 hours at 750℃ ; Cat C (3 hours at 950℃ ) & Cat S (20 minutes at 950℃ ).
Resistance to fire with water spray – a new sample of cable is exposed to flame at 650℃ for 15 minutes while passing a current at its rated voltage and then the spray is turned on to give exposure to both fire and water for a further 15 minutes. A single survival category W is defined if the cables surpassed the testing requirement.
Resistance to fire with mechanical shock – the final requirement is mechanical shock damage. A fresh sample is mounted on a backing panel in a S bend and is exposed flames while the backing panel is stuck with a steel bar with same diameter as the cable under test every 30 seconds for 15 minutes. The cables will be tested under the following temperatures: X (650℃ ), Y (750 ℃ ) and Z (950℃ ).
8
另,我附上時(shí)性膠料燃燒測(cè)試和電線(xiàn)燃燒測(cè)試相關(guān)內(nèi)容,以供大家更加全面的了解.
一、可燃性UL94等級(jí)是應(yīng)用最廣泛的塑料材料可燃性能標(biāo)準(zhǔn)。它用來(lái)評(píng)價(jià)材料在被點(diǎn)燃后熄滅的能力。根據(jù)燃燒速度、燃燒時(shí)間、抗滴能力以及滴珠是否燃燒可有多種評(píng)判方法。每種被測(cè)材料根據(jù)顏色或厚度都可以得到許多值。當(dāng)選定某個(gè)產(chǎn)品的材料時(shí),其UL等級(jí)應(yīng)滿(mǎn)足塑料零件壁部分的厚度要求。UL等級(jí)應(yīng)與厚度值一起報(bào)告,只報(bào)告UL等級(jí)而沒(méi)有厚度是不夠的。UL94中共有12種:HB、V-0、V-1、V-2、5VA、5VB、VTM-0、VTM-1、VTM-2、HBF、HF-1、HF-2。塑料阻燃等級(jí)由HB,V-2,V-1,V-0,5VB向5VA逐級(jí)遞增:
HB:UL94標(biāo)準(zhǔn)中最底的阻燃等級(jí)。要求對(duì)于3到13 毫米厚的樣品,燃燒速度小于40毫米每分鐘;小于3毫米厚的樣品,燃燒速度小于70毫米每分鐘;或者在100毫米的標(biāo)志前熄滅。
V-2:對(duì)樣品進(jìn)行兩次10秒的燃燒測(cè)試后,余焰&余燃在60秒內(nèi)熄滅。滴落的微?牲c(diǎn)燃棉花。
V-1:對(duì)樣品進(jìn)行兩次10秒的燃燒測(cè)試后,余焰&余燃在60秒內(nèi)熄滅。滴落的微粒不可點(diǎn)燃棉花。
V-0:對(duì)樣品進(jìn)行兩次10秒的燃燒測(cè)試后,余焰&余燃在30秒內(nèi)熄滅。滴落的微粒不可點(diǎn)燃棉花。
5VB: 對(duì)樣品進(jìn)行五次5秒的燃燒測(cè)試后,余焰&余燃在60秒內(nèi)熄滅。滴落的微粒不可點(diǎn)燃棉花。對(duì)于塊狀樣品允許被燒穿.
5VA: 對(duì)樣品進(jìn)行五次5秒的燃燒測(cè)試后,余焰&余燃在30秒內(nèi)熄滅。滴落的微粒不可點(diǎn)燃棉花。對(duì)于塊狀樣品不允許被燒穿.
二、電線(xiàn)燃燒方式:
VW-1:垂直燃燒測(cè)試(UL電線(xiàn)燃燒等級(jí))
FT1:垂直燃燒測(cè)試;
FT2:水平燃燒測(cè)試;
FT4:垂直燃燒測(cè)試;
FT6:水平燃燒和煙熏測(cè)試。(FT類(lèi)的燃燒等級(jí)是CSA標(biāo)準(zhǔn)的電線(xiàn)燃燒等級(jí))
以上級(jí)別中:VW-1與FT1同一個(gè)等級(jí),F(xiàn)T2最容易通過(guò),等級(jí)最低.(FT6>FT4>FT1>FT2);VW-1嚴(yán)格于 FT1,二者都是垂直燃燒,判定標(biāo)準(zhǔn):
1) 燃燒標(biāo)記(牛皮紙)不能被炭化超過(guò)25%;
2)5次15秒的燃燒續(xù)燃時(shí)間不能超過(guò)60秒;
3)燃燒滴落物不能引燃棉花;
VW-1要求滿(mǎn)足1,2,3; FT1只要求滿(mǎn)足1,2
三、對(duì)于電線(xiàn)行業(yè)來(lái)說(shuō)UL 94 的 V-2, V-1, V-0, 5VA,5VB考核的是電線(xiàn)所用的材料,測(cè)試時(shí)要另外用測(cè)試材料制定標(biāo)準(zhǔn)樣本,不會(huì)在電線(xiàn)上標(biāo)識(shí)。VW-1 VW -2 FT-1 FT-2考核的是電線(xiàn)本身,測(cè)試通過(guò)后,可以在電線(xiàn)上標(biāo)識(shí)對(duì)應(yīng)的等級(jí)。電線(xiàn)的阻燃跟UL94的阻燃完全是兩個(gè)不同的東西,打個(gè)比方 一種絕緣材料能通過(guò)UL94的V-0 但不一定就能通過(guò)VW-1;另外UL94是絕緣材料的阻燃,而電線(xiàn)的阻燃要求一般是在UL758 62 1581上,對(duì)象不同;所以V-0 V-1等UL94里面的阻燃根本就不是電線(xiàn)的阻燃;在AWM線(xiàn)材上就沒(méi)有印“V-0”! UL94燃燒試驗(yàn)中有HB、V0、V1、V2、VMT、5VA、5VB等燃燒試驗(yàn),而UL1581中有VW-1、FT1、FT2、FT4等燃燒試驗(yàn),這二大試驗(yàn)在設(shè)備上的區(qū)別如下:
VW-1\FT1噴燈為:125mm(500W)、燃燒火焰:內(nèi)焰高度40±2mm,外焰125±10mm
UL94 HB、V級(jí)噴燈為:20mm(50W),燃燒火焰:藍(lán)焰內(nèi)無(wú)錐形,高度20±1mm
UL94中的5V級(jí)燃燒是采用125mm(500W)、燃燒火焰:內(nèi)焰高度40±2mm,外焰125±10mm
火焰的火焰溫度也不一樣:20mm(50W)試驗(yàn)火焰:100±2~700±3℃的時(shí)間是44±2S;125mm(500W)試驗(yàn)火焰:100±2~700±3℃的時(shí)間是54±2S。
試驗(yàn)空間也不一樣:UL94中的HB、V、VMT其空間只要求大于0.5立方就可以,而5V要求大于0.75立方,VW-1要求大于4立方。
甲烷的流量要求不一樣:HB級(jí)、V級(jí)、VMT級(jí)燃?xì)饬髁繛?05ml/min,背壓力10mm水柱或相等壓力;5V級(jí)燃?xì)饬髁繛?65ml/min,125±25mm水柱或相等壓力,VW-1與UL94中的5V級(jí)背壓力一樣:燃?xì)饬髁繛?65ml/min, 125±25mm水柱或相等壓力。(注意:目前國(guó)內(nèi)很多的塑料UL94燃燒機(jī)并沒(méi)有配備專(zhuān)用的甲烷流量計(jì)(常常用空氣流量計(jì)代替,從而造成很大差異。,另外也沒(méi)有配備U型背壓力計(jì)!,更重要一點(diǎn)是:沒(méi)有配備火焰測(cè)溫系統(tǒng)。UL94中的5V級(jí)燃燒與VW-1燃燒的試驗(yàn)條件與試驗(yàn)方法差不多,比較接近!提醒大家:不管是VW-1還是UL94燃燒試驗(yàn)設(shè)備,都得參照ASTM5025與ASTM5027,UL1581與UL94只是試驗(yàn)方法,試驗(yàn)設(shè)備的要求一定要按ASTM標(biāo)準(zhǔn)!